If you are experiencing a [C] fault on the CACR-PR30 CSY166C it could be caused by a defective motor/encoder assembly. However, we have discovered that on this 166C model that the cause may be a factory setting that is not correct. The setting is the SW1 header jumper located inside the drive. This header selects the motor type and is typically set for a USASED type motor. The setting for use in a GSM machine X axis is unconventional because the motor is a custom motor and therefore the setting found in the users manual showing sw1-4 installed if sw1-1 or sw1-2 is installed is incorrect.
The CACR-PR30 CSY166C SW1-4 jumper must be out for the X and Y axis use despite this jumper being specified in Yaskawa documentaion as required when SW1-1 or SW1-2 being installed. We test using this jumper installed but the client must have this jumper removed for this drive to function correctly in the GSM machine because the motor on the machine is a custom.